StoreOnce Gen4
StoreOnce3620
StoreOnce3640
StoreOnce5200
StoreOnce5250
StoreOnce5650
GUI中显示两块P1228都是Failed状态.
系统运行正常, 可以进行数据备份.
P1228的电池, Cache和Port都是Faield状态.
iLo中显示两块P1228的状态都是Unknown, 这是正常的显示状态.
显示Unknown是由于iLo没有P1228的驱动, 并不表示是Failed状态.
StoreOnce 5200 FW4.1.3
Jan 8 20:22, StoreOnce系统跟iLO失去通信
Jan 8 20:22:35 ALERT The server status cannot be determined due to an inability to communicate with the iLO. hpspmon-event-message SERVER_ILO_NO_CONNECTION Ensure that the iLO idle timeout is set to 30 minutes or less. Attempt to reboot the iLO if accessible via Ethernet. Otherwise shut down the server, pull the power plug on the server, restore power to the server and boot to operational mode.
紧接着系统提示P1228 controller missing or failed.
Jan 8 20:22:35 ALERT The controller is missing or has failed. hpspmon-event-message CONTROLLER_MISSING Try rebooting the server or reseating the controller. If you succeed, please examine the controllers lockup log to see if a firmware fault was encountered.
实际上Storage是正常状态, 数据备份可以正常进行, 综合来看, 不是硬件故障, 而是系统间的通信出现异常, 导致系统不能正常检测到硬件的信息.